Recent Valves, Actuators & Regulators Discussions
mark.nymeyer
7 Sep 2020 6:49 AM
Article: Wireless Monitoring Improves Power Plant Operations - Power Jun 2019
1 Reply
mark.nymeyer
20 Aug 2020 7:48 PM
Article: Hydrocarbon Engineering Aug 2020, Ways and Means: Control Valve sensor data and IIoT offer a new way to help users improve control valve performance and predict problems.
0 Replies
mark.nymeyer
21 Jul 2020 3:34 PM
Article: Protect Control Valves When Production Slows
0 Replies
mark.nymeyer
18 Jun 2020 2:36 PM
Many manual process automation applications can be converted to real-time wireless control, providing significant savings and other operational improvements.
0 Replies
mark.nymeyer
29 Apr 2020 2:42 PM
Article: The Basics of Desuperheating and Steam Conditioning
0 Replies
<
>
Similar Posts
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Effective Use of FIELDVUE™ DVC6200 Instrument Diagnostics HART® Communication Protocol
DVC6200 SIS HART capabilities
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.