Recent Valves, Actuators & Regulators Discussions
mark.nymeyer
18 Jan 2021 3:12 PM
Article: Selecting the Right Rotary Control Valve
0 Replies
mark.nymeyer
15 Jan 2021 4:52 PM
Article: Overcoming Control Valve Trim Selection Challenges
0 Replies
mark.nymeyer
12 Jan 2021 5:53 PM
Article: Meeting New Methane Emission Standards Profitably
0 Replies
mark.nymeyer
8 Oct 2020 12:15 AM
Article: Unanticipated cavitation can destroy a control valve’s internals and even result in catastrophic failure, so it is important to understand what cavitation is, why it occurs, and how to address.
1 Reply
Gerard Nagle
29 Sep 2020 7:24 PM
Pressure relief valve Engineering handbook error?
1 Reply
<
>
Similar Posts
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Effective Use of FIELDVUE™ DVC6200 Instrument Diagnostics HART® Communication Protocol
DVC6200 SIS HART capabilities
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.