No unit phases or Phase logic modules error during OP verification

Hello Experts,

I was following a painting tutorial and created an operation called OP_FINISH. However, when I assigned it to the Batch Executive and attempted verification, it resulted in an error message.

I understand that the assigned unit class has phases that include the phase logic, as I have tested these phases during the phase testing section of the tutorial.

Any assistance would be appreciated.

Thank you in advance.

  • All Unit Instances that would be assigned would need the AGITATE and DRAIN phases marked as controller. Also make sure that the unit instances are under Process Cells that are linked to a Process Cell Class and the area that the unit instances are assigned is assigned to the batch executive.
  • In reply to Matt Stoner:

    Thank you, Matt, this worked. All the phases under unit instances were already marked as 'controller', and the process cell was also linked to the process cell class. The only pending item was that the area had not been assigned to the batch subsystem. Once the area was assigned and the recipe verified, all the checks passed.