The post Getting Automation Started by Selection of Control Action and Modes first appeared on the ISA Interchange blog site.
Pulp and paper plant studies found 75 percent of the loops caused more variability in the automatic mode than in the manual mode. A third of them oscillated as a result of nonlinearities such as valve dead band. Another third oscillated because of poor controller tuning. The remaining loops oscillated because of deficiencies in the control strategy. A well-designed control loop with proper tuning and a responsive control valve can minimize this variability. Because this means you can operate closer to constraints, good tuning can translate into increased production and profitability.
Actions Speak Louder than Words
The very first settings that must be right are the controller and valve actions. If these actions are not right, nothing else matters. The controller output will run off scale in the wrong direction regardless of the tuning settings.
The controller action sets the direction of a change in controller output from its proportional mode for every change in the controller’s process variable (feedback measurement). If you choose direct action, an increase in process variable (PV) measurement will cause an increase in controller output that is proportional to its gain setting. Since the controller action must be the opposite of process action to provide feedback correction, you should use a direct-acting controller for a reverse-acting process except as noted later in this guide.
Correspondingly, you should select reverse control action for a direct acting process so an increase in process variable measurement will cause a decrease in controller output that is proportional to its gain setting, except as noted later. A direct-acting process is one in which the direction of the change in the process variable is the same as the direction of the change in the manipulated variable. A reverse-acting process is one in which the direction of the change in the process variable is opposite the direction of the change in the manipulated variable. The manipulated variable is most frequently the flow through a control valve, but it can also be the set point of a slave loop for a cascade control system or variable speed drive.
The valve action sets the display. For example, it determines whether a 100 percent output signal corresponds to a wide open or a fully closed valve. It also determines the direction of a change in the actual signal to the control valve when there is a change in the controller’s output. In some analog controllers developed in the 1970s, such as the Fisher AC2, the valve action affected only the display of the valve signal, not the actual signal. To compensate for this lack of signal reversal for a reverse-acting valve (i.e., an increase-to-close or fail-open valve), the control action had to be the opposite of the action that would normally be appropriate based on process action alone.
Fortunately, the valve action corrects both the display and the actual valve signal in modern controllers, so the control action can be based solely on process action. However, the user should verify this before commissioning any loops. In control systems that use fieldbus blocks, the valve action should be set in the analog output (AO) block rather than in the PID controller block. This ensures that the “back-calculate” feature is operational for any function blocks (split range, characterization, and signal selection) that are connected between the PID and AO blocks. The signal can also be reversed in the current-to-pneumatic transducer (I/P) or in the positioner for a control valve. Before the advent of the smart positioner, it was preferable for the sake of visibility and maintainability that any reversal be done in the control room rather than at the valve. Reversal of signal in the control room is still advisable to prevent the wrong fail action for a scenario where you lose the field signal to the positioner but not the power to the positioner. In this case, the positioner could possibly reverse the signal to the actuator causing an “Increase-Close” valve to close. It is important to standardize on the location of the signal reversal to ensure that it is done and done only once. Table 1 summarizes how the controller action depends upon both the process and valve actions and on the signal reversal.
Table 1: Controller Action
Which brings us to a rule of thumb:
The controller action should be the opposite of the process action unless there is an increase-to-close (fail-open) control valve for which there is no reversal of the valve signal. This means that you should use reverse and direct-acting controllers for direct and reverse-acting processes, respectively. The valve signal can be reversed for a fail-open valve at many places, but it is best done in the AO block of the control system.
Controller à la Mode
The names for the operational modes of the PID vary from manufacturer to manufacturer. Thus, the Foundation™ Fieldbus modes listed next provide a uniformity that can be appreciated by all.
Anyone setting up a PID controller must select the correct control action and enable the proper choices of control modes including the right normal mode and initial mode.
To make sure the PID setup is correct, one must verify by field tests and conferring with instrument design and maintenance, operators, and the process engineer whether the process is reverse acting or direct acting and whether the valve is fail open (increase-to-close) or fail close (increase-to-open). One must also find out from the person who configured and tested the PID and control valve I/P and positioner if the valve signal is reversed anywhere. The signal should only be reversed for an increase-to-close valve and the reversal should be done at one point only. Provided there is no improper or missing signal reversal, the control action should be the opposite of the process action to give the negative feedback action necessary to achieve stability.
In general, the manual mode should never be taken away from the operator because there are too many unforeseen possibilities and the operator is the last defense for safety and stability. There is nothing worse than an operator feeling powerless. The initial mode is chosen based on what mode is appropriate for a total download and startup. The normal mode is the mode desired for best performance. Secondary PID controllers must have the Cascade mode permitted in order for the primary PID controller to manipulate the secondary controller setpoint. For intelligently prepositioning of the PID output for sequences and to preemptively deal with situations and optimization of the output for setpoint changes, the remote output mode should be permitted. Finally, when PID setpoint is being intelligently adjusted or optimized (e.g., override control, valve position control, model predictive control, or supervisory control), the remote cascade mode is permitted.