Control systems provide signals to control valves to regulate their position per the requirements of the control strategy. It is good engineering practice, especially for critical control valves to have valve travel feedback from independent devices such as position transmitters, limit switches, or positioner output feedback.
Emerson’s Riyaz Ali, whom you may recall from earlier posts, shared ways this position information can be fed back to the operators at their operator workstations.
Actual travel feedback of control valve can be viewed in the DCS by following means:
Riyaz noted that new, greenfield project could make the decisions upfront on which technology to use for this valve travel feedback. Existing brownfield installations may have challenges installing these devices on the existing control valves. If the control system has either HART pass-through capabilities or the Foundation fieldbus communications protocol, the option likely exists to get travel feedback.
If the existing control valve with has a smart, HART-based positioner, there is a possibility that a position feedback option exists or you can add HART TriLoop or HIM (HART Interface Module) to extract travel information. If none of these options are available another path would be to install independent position transmitters, limit switches, or wireless position monitors.
Wiring can be a challenge in existing plants. To install the position feedback option to existing smart, HART-based positioner or to install a position transmitter or limit switch, the following steps must occur: laying wire, cable tray or conduit from field to the control system, using spare or inserting new I/O card for digital or analog signals, conduit connections, changing drawings to show wiring and I/O, barriers, and power supplies. Also, costs include the labor for installation and commissioning these feedback devices.
Riyaz explained that wireless is a smart field device communications technology that has been established over the past several years and is straight forward, reliable and overcomes the constraints faced with wired approaches.
Wireless field device networks require:
These networks support organic growth over time as monitoring needs dictate and they can overlay over any installed infrastructure. Here are links to the Fisher 4320 wireless position monitor and HART-based wireless THUM adapter for additional information.
You can connect and interact with Riyaz and other experts in the Valve Controllers & Positioners track of the Emerson Exchange 365 community.
The post Providing Operators Process Control Valve Position Feedback appeared first on the Emerson Process Experts blog.