Hi Group
Is it possible to create a class unit parameter connection to equipment control module class parameter? what connection format should be used in my EM?
Below image is describing what I want to achieve
Thanks for your support
Not sure what you try to achieve. Are you trying to access a Control Module parameter from an EQM using a Unit parameter as intermediary??
A nice feature of deltav class based configuration is that you can use aliases into equipment modules directly. You can code any expression inside EQM class in the form #ALIAS_NAME#/PATH_TO_PARAMETER_NAME. To allow this it is required to place EQM instance inside UNIT instance (see attachment).
So that intermediate unit parameter is not really required.
Both EQMs into screenshoot may have code using parent UNIT aliases. In example: #TCIP_104#/LEVEL_PV