Hi All,
I am looking to have a landing module in one controller for profibus I/O that is physically located on another controller.
I am running DV version 12.3.1 on both controllers. When i try and write to an output parameter set as external reference, with external reference path set to the DST for the I/O, the value will not populate across. I seem to be able to receive data into the landing module from the external I/O DST's but not send.
Is this related to firmware on the I/O module? Controllers were upgraded to 12.3.1 but the I/O cards have not been done.
The landing module is assigned to the controller that does not contain the physical I/O. I have found that if i create an extra module and assign it to the controller that does contain the physical I/O and write to a input parameter within it and pass this to an output parameter with external reference set to the I/O DST the value is written to the I/O.
This is a work around but i thought it should be possible to write directly to the DST in the second controller.
Thanks
Tony_M