Recent Valves, Actuators & Regulators Discussions
Emerson Exchange News
30 Sep 2019 3:14 PM
JXTG boosts valve reliability with Connected Services
1 Reply
mark.nymeyer
15 Aug 2019 9:01 PM
Article: Valve Sourcing Goes Global
0 Replies
mark.nymeyer
25 Jul 2019 4:46 PM
Article: Valve World magazine interviewed Chris Hammond, an engineer in Emerson’s Severe Service valve group in Marshalltown, Iowa.
0 Replies
mark.nymeyer
1 May 2019 1:03 PM
Article: Flow Control, April 2019, Specifying Ball Valves in Pipeline Applications
0 Replies
mark.nymeyer
1 May 2019 12:51 PM
Article: The Case for RFID In Process Plants
0 Replies
<
>
Similar Posts
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Effective Use of FIELDVUE™ DVC6200 Instrument Diagnostics HART® Communication Protocol
DVC6200 SIS HART capabilities
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.