Recent Valves, Actuators & Regulators Discussions
hast66
2 Oct 2021 5:39 PM
serial cards question
0 Replies
James Doell
17 Sep 2021 12:43 PM
Flow control valve specs
3 Replies
mark.nymeyer
30 Aug 2021 8:44 PM
Article: Choked Flow in Control Valves
0 Replies
mark.nymeyer
7 Jul 2021 2:16 PM
Article: Switching on to Electric Control Valves’ Potential#
0 Replies
mark.nymeyer
29 Jun 2021 11:45 PM
Article: Advanced Valve Diagnostics Drive Savings
1 Reply
<
>
Similar Posts
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Effective Use of FIELDVUE™ DVC6200 Instrument Diagnostics HART® Communication Protocol
DVC6200 SIS HART capabilities
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.