Recent Valves, Actuators & Regulators Discussions
Jeff Roseneder
2 Nov 2017 3:30 AM
VIDEO: Best Practices for Lowering Fugitive Emissions Caused by Valves
3 Replies
Vijay Sarathy
1 Nov 2017 7:07 PM
Anti surge design and Sizing
0 Replies
Adin Mann
24 Oct 2017 3:26 AM
VIDEO: Vibrations – Stop Them or Use Them?
1 Reply
Riyaz Ali
19 Oct 2017 2:59 PM
VIDEO: Final Element Proof Testing for Safety Instrumented Functions
0 Replies
Jim Cahill
19 Oct 2017 6:29 AM
Valve Health Diagnostics and Tips
1 Reply
<
>
Similar Posts
new DVC not communicating with HART communicator
Interrogating a DVC type HC positioner with a HART 475 communicator
DVC6030 - HART Not Communicating at 20mA with SLS Two-state output channel?
Effective Use of FIELDVUE™ DVC6200 Instrument Diagnostics HART® Communication Protocol
DVC6200 SIS HART capabilities
Share
Answered
Use of 250ohm resistance in HART Communication?
Why is it necessary to use a 250ohm resistance in HART communication?
All Responses
Answers Only
Jonas Berge
16 Dec 2014 11:50 AM
It doesn't have to be exactly 250 ohm. Anything from 230 - 1100 ohm will do
The reason it is required is that the HART signal is transmitted as a current and received as a voltage. The resistor works as a shunt that converts the transmitted current to a voltage the other device receives. The second reason it is required is because a DC power supply will short circuit the AC HART signal. The resistor prevents this from happening.
Note that this resistor is only required for transmitters. It is not required for positioners.