Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5484 subscribers
Views
9626 views
Users
0 members are here
Related Posts
RESTORING PARAMETERS AFTER POWER FAILURE
RET or CALC block in SFC type of Composite Template
Integrator Function - run hours restore value after bad reset
Restore parameter values after de(re)comissioning of controller
Webinar on April 16th about well closure and restoration after hydraulic fracturing
Share
Restoring RET function block accumulated time after power failure
We use the RET function block to control change sequence for drier unit. All is working perfectly except the fact that after a power failure or controller download the RET count is reset to zero thereby forcing the sequence to start from beginning.
We have enabled the "Restore parameter values after restart" but the problem persist.
Kindly assist with suggestions on how to solve this problem.
Thank you
1 Reply
GeloCortez
7 Jul 2016 8:38 AM
try "Preserve user define and critical block values"